redwood1957
Now plumbers are cutting into copper lines and running pex tubing who or is anyone required to bond the old copper that is fed with pex? Its like running metal conduit and switching over to pvc with out providing a ground
redwood1957 said:Now plumbers are cutting into copper lines and running pex tubing who or is anyone required to bond the old copper that is fed with pex? Its like running metal conduit and switching over to pvc with out providing a ground
jwelectric said:I didn?t start saving the ROPs until the 2002 cycle. I wish I could get my hands on them all.
This topic is one of my favorite to debate as there is no clear verbiage that mandates that a metal water pipe be made electrically continuous.
As Bob (iwire) pointed out there are some who believe that there could be different systems contained in the same system.
The problem I see with this thinking is; any piece of metal pipe would become a system in and of itself making it a requirement to bond the short stubs.
The way I read and interpret article 250 is there is only one case where the metal water pipe is required to be make electrically continuous and that is found in 250.53(D)(1). Here the only part of the metal water pipe that is required to be made electrically continuous is that part where the bonding jumpers and electrode conductor are terminated to earth.
During the same cycles of the NEC where it was required that the metal water system be continuous a three wire receptacle could be replaced and the EGC ran to the nearest water pipe. The same year that the words ?made electrically continuous? were removed from 250-80 the relief to run the EGC form a three wire receptacle was removed from 250.50(b) Exception. Allowing the EGC from a replacement receptacle to land on the water pipe was removed in 1993. 250-50(b) Exception is 250.130 in the 2005 cycle. If it was still the intent for the metal water pipe to be electrically continuous there would have been no need to remove the wording from 250.50(b) Exception and this would still be allowed in 250.130 today.
Based on these findings and the language found in 250.53(D)(1) and 250.104(A)(1) I can?t help but to believe that it is no longer the intent that the metal water pipe be electrically continuous.
The original electrician, if he never installed a supplemental electrode.hillbilly said:Along comes a plumber and replaces the underground portion with plastic and un-knowingly eliminates the GE.
If he cuts the metal line before the connection to the Grounding Electrode Conductor (GEC), the interior plumbing remains bonded to the service, but the house doesn't have a Grounding Electrode anymore.
Who's to blame?
Who's to blame?
LarryFine said:The original electrician, if he never installed a supplemental electrode.
TwinCitySparky said:If there is any possibility that the copper could become energized, then I'd bond it.
You don't have to bond the nails if they're supplied through GFCI devices.jim dungar said:If we have to bond every metallic item that possibly could become energized, we would have to bond the nails used for hanging pictures. After all, they must have the possibility of becoming energized, otherwise we would not need to use "nail plates".
LarryFine said:You don't have to bond the nails if they're supplied through GFCI devices.
As long as they're the combo type, yes.jim dungar said:Would an AFCI be okay instead?![]()
jim dungar said:Then you would be going above and beyond what is required.
The NEC requires bonding only if it is probable that the copper will be energized.
TwinCitySparky said:Well I guess I'm glad I'm not being accused of going below and falling short.
- I was thinking of the typical "handyman special" basements that I often get sent into where the plumbing looks to be the basic support system of all the romex - and they had the pex entry changeover...
TwinCitySparky said:Sure.
Again... Imagine the typical Joe homeowner basement where many DIY types or "handypeople" have ran plumbing thru (and mostly below) the floor trusses, supporting it with nail on hangers etc. Take lots of romex and pull it through (above and below) that whole mess in a spagetti like fashion. Then, take a metal supported pop in ceiling tile system and CRAM whatever wont fit on top of that. Finally add some non-stop energetic kids to the mix for some endless artificial sizemic activety.
Sharp edges/romex and jarring motions. Not a good mix. I've seen damages romex many times in these situations.
That is why I use the standard code methods of support - i.e. conduit, bored holes, straps.
Take a few feet of copper (if po$$ible) and bond the whole mess (if not already bonded). Explain it to the customer. They appreciate your above and beyond concern. They know you are looking out for their safety, they call you back next time. Happy customers...
No bid deal.
Fried? Food? Good pun.R Bob said:Fortunately, the guy wasn't found fried inside of the AHU.
Just food for thought.