Plumbing PVC as a chase?

Status
Not open for further replies.

The Iceman

Senior Member
Location
Florida
Is it wrong to use a 10' plumbing PVC, as a chase for MC, from an exposed ceiling to a work station? The only code I could find is 300.8 but thats only Installation of conductors with other systems.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
IMO, there is no problem, it is only a chase.

Roger
 

nakulak

Senior Member
its fine until someone comes along and thinks they are cutting a piece of plumbing pipe away only to get electrocuted. If you are going to use pvc why not use something that indicates that there are probably wires in it ?

on second thought,

I think this violates
110.12 (workmanlike manner)
330.10 - It does not list plumbing pipe as an approved raceway for mc (where it says "in any raceway" it presumably means "in any NEC recognized raceway", ie a chapter 3 or otherwise listed raceway)
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
According to the NEC this perfectly legal as long as you're pulling cables through it and not individual conductors. Individual conductors would require a listed raceway.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
nakulak said:
its fine until someone comes along and thinks they are cutting a piece of plumbing pipe away only to get electrocuted. If you are going to use pvc why not use something that indicates that there are probably wires in it ?

It's an "EXPOSED CEILING", if a person cuts into this chase without looking up they will probably die from something stupid anyways. :rolleyes:


from an exposed ceiling to a work station?


Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
nakulak said:
I think this violates
110.12 (workmanlike manner)

Not enforcible.


nakulak said:
330.10 - It does not list plumbing pipe as an approved raceway for mc (where it says "in any raceway" it presumably means "in any NEC recognized raceway", ie a chapter 3 or otherwise listed raceway)

So, is a stud cavity in a wall between floors an approved raceway?

If the MC is fished in any existing pipe, abandoned chimney, purposely designed sheetrock chase, abandoned dumbwaiter shaft, etc... it's legal.

Roger
 