Hi everyone! Have received many good comments in the past. I have a single phase exhaust fan for commercial kitchen. motor is 115/230-Capacitor start motor. 19.6 amps/9.8@230.Iwired for 115V. Ran #10,s Have 30 amp 2HP rated switches, One for disconnect@motor and one at hood. Voltage at panel is 114V. voltage at motor is 112V. voltage drop meets 3% allowance per NEC.(less than3.6V) This motor is fed from a sub-panel. I have 114V on phase A,118V. on phase B. Went to service and found same voltage from each phase. Amps=21.2 under load. I tried to look up model # under Granger supply to see if there is a plus or minus allowance for this motor. Problem is , Exhaust runs all day for customer, but at some point the integral thermal overload kicks out. Has to cool down, then can be re-started. Breaker never trips. I want to swap phases so motor will have specified operating voltage on nameplate. Motor is rated cont. duty with 1.15 SF. I,m thinking motor is bad. Company that installed this told me the problem is on my end. Thanks much!!