- Mission Viejo, CA
- Professional Electrical Engineer
I received the following PM
Your statement, "according to NEC code the max length of Liquid tight flexible metal conduit(LFMC) in CLASS 1 DIV. 2 is 6ft ", isn't entirely correct either. Six feet is the maximum for LFMC with an external bonding jumper. See Section 501.30's cross reference: 250.102, especially 250.102(E).
I honestly don't know the full history, but at one time CMP14 was absolutely paranoid about grounding/bonding in all classified locations. I agree with the bonding level required for Class I, Division 1; Class II, Group E and disallowing locknut and locknut/bushing bonding. My personal opinion is the requirements are a bit overkill otherwise - but they are the requirements.
The practical problem is you have increased the maximum allowable length 33%. In truth, it has more to do with the limits of the UL test standards; they just don't test lengths longer than 6'.stev11 said:hi
can you please help me for this question??
But what is the practical problem if I connect 8ft instead of 6 ft??? is this will make explosion in CLASS 1 DIV. 2 location ???(note: I know this is not acceptable for NEC code but I need to understand )
thank you.