I have always had the understanding that pneumatics and control wiring are not to be located in the same conduit run. Is this just a rule of thumb or is it actually in the NEC? If it is code, where is it referenced?
300.8 - keep in mind that that is for conductors that must be installed in a raceway. There is nothing wrong with installing pneumatic lines and listed cables that are not required to be in a raceway in some type of tubing, tray, or whatever that is there for support or physical protection.
Can you point us to where we can find this permission?
Roger
How about telling me where it is not permitted.
Raceways or cable trays containing electrical conductors shall not contain any pipe, tube, or equal for steam, water, air, gas, drainage, or any service other than electrical.
I see conductors as wires that need to be in a raceway, IMO if 300.8 meant to include cables it would say cables.
that doesn't tell me these conductors enclosed within an overall nonmetallic jacket are exempt from article 300.8.Nonmetallic-Sheathed Cable. A factory assembly of two or more insulated conductors enclosed within an overall nonmetallic jacket.
If you put a divider in a cable tray, is it now considered two separate trays for the purpose of running conductors/wires/hoses?
I agree with Roger
NEC Article 300.8. Raceways or cable trays containing electrical conductors cannot contain elements of other systems?no water pipes, gas pipes, or any other non-electrical system elements can run in those electrical wireways.
Air line is non Electrical isn't it?
And where can we find supporting code words for this?
Bob
I was not addressing any certain individual, but I think that is one of the plainess statements I have read in the NEC. Non electrical is non electrical, sorry you took it personnel.
Ronald
Bob
I can see the logic with conduit but not necessarily with tray.
Bob
I can see the logic with conduit but not necessarily with tray.
If you had a pneumatic Thermostat line run in a conduit with a fault in it,it could melt a hole in the air line and you would loose temperture control of those units or unit.
Why take that chance?