Large car wash will experience random outages caused by a POCO overhead transformer fuse melting. This happens a few times a year.
I am adding a voltage recorder on the secondary this week.
The service is 400A, 480Y/277. POCO has three 100kVA transformers fused 15T on 24.9Y/14.4kV.
The general rule is this fuse melts at X2 the rating after five minutes. This time only one transformer fuse melted but have seen all three melted at the same time.
That math is 432kVA at least.
The attendant said the large drying fans were running, turned off and when they restarted, the fans were still turning. That is when the POCO fuse melted.
A thought I had was the turning motor acts a generator and when the contactor closes to start that motor again, the voltages are not in synch.
The first thought was a turning motor would reduce inrush because it was already turning.
The attendant said they have a similar random issue at another one of their locations.
Possible?
A motor restart time delay has worked on turbine water well sites that melted POCO transformer fuses.
Thanks,
I am adding a voltage recorder on the secondary this week.
The service is 400A, 480Y/277. POCO has three 100kVA transformers fused 15T on 24.9Y/14.4kV.
The general rule is this fuse melts at X2 the rating after five minutes. This time only one transformer fuse melted but have seen all three melted at the same time.
That math is 432kVA at least.
The attendant said the large drying fans were running, turned off and when they restarted, the fans were still turning. That is when the POCO fuse melted.
A thought I had was the turning motor acts a generator and when the contactor closes to start that motor again, the voltages are not in synch.
The first thought was a turning motor would reduce inrush because it was already turning.
The attendant said they have a similar random issue at another one of their locations.
Possible?
A motor restart time delay has worked on turbine water well sites that melted POCO transformer fuses.
Thanks,