POCO Power Cable to my house

Status
Not open for further replies.

charlie

Senior Member
Location
Indianapolis
Re: POCO Power Cable to my house

The NESC requires 24 inches of cover. The various electric utilities may require more but never less. IPL requires a 36" deep trench to put the cable into and allows up to 4" of grading after installation. :D
 

dcsva@aol.com

Senior Member
Location
Virginia
Re: POCO Power Cable to my house

We accidentally dug it up today and we were only about 18" down. I knew the power line was there so we were being very careful, I was very concerned when we came across it soooooo early.
 

dcsva@aol.com

Senior Member
Location
Virginia
Re: POCO Power Cable to my house

The meter is mounted to the back of my house near the back entrance door. The power extension comes from the far back left corner of the property. Approx. 100FT
 

ron

Senior Member
Re: POCO Power Cable to my house

Did you dig a section on the utility side of the meter, or your side of the meter. If utility side, then NESC. Your side, then NEC. The NEC would have required 18" in PVC.
 

charlie

Senior Member
Location
Indianapolis
Re: POCO Power Cable to my house

It was a PVC outer shell
It could have been "cable in conduit" which would have been a black HDPE conduit. Of course, it could have been PVC. Anyway, the NESC says in Rule 352D2b "Lesser depths that indicated above may be used where supplemental protection is provided. The supplemental protection should be sufficient to protect the cable from damage imposed by expected surface usage."

The bottom line is that the cable, whether protected or not, should have been located before digging. I suspect you will be required to pay the piper. :(
 

gwz2

Senior Member
Location
Indiana
Re: POCO Power Cable to my house

Hi Charlie,

I know you are electrical.

Do you have any IURC info on gas line depths.

On a Sunday, years ago I was roto-tilling, at no more than 6 inches and dug-up and cut-into the gas line.

That was the servicemans' first words also.

I suppose I was lucky and never heard about the service charge again, but at 6" ??.
Actually the Gas pipe was only down about 4".

The Poco's, CATV's, and Telephone services should be required to be down at least 24" to the top of their laterals, but what does the URC say?

edit " forgot to include Gas service lines. "

[ April 21, 2003, 07:48 AM: Message edited by: gwz2 ]
 

torint

Member
Re: POCO Power Cable to my house

Is it a code that you put red electrical caution tape in the trench several inches above the conductor? I was taught to alway's put it in for safety...if its not a code then it should be.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: POCO Power Cable to my house

torint,
Marking is only required for undergound service conductors that are not encased in concrete and not installed by the utility. See 300.5(D)(3).
Don
 

torint

Member
Re: POCO Power Cable to my house

Don, I read 300.5(D)(3). Thank you for showing me that. I have read many of your scripts that say the code is a bare min and I agree. What are your feelings on making it a code requirement to place a warning ribbon on all buried conductors? For the sake of safety and to warn others from causing a disruption of power. I do it all of the time and even the home owner that is planting bushes or re cementing yards will have a "heads up". :)
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: POCO Power Cable to my house

DC

I would bet that the grade was changed after the installation. Was the unearthing at the driveway?

My POCO places the underground at 4' and requires schedule 80 any place it cross a driveway.

Mike P.
 
Location
Virginia
Re: POCO Power Cable to my house

okay...okay...
we were digging because we got a bob-cat stuck up to its belly when we were spreading some crush-n-run to extend the driveway to the back yard.
The power line was about one-foot outside the edge of the drive and would not go under crush-n-run surface. But we got stuck, As soon as I saw the power line we hooked chains to its bucket and choked the chain around a big tree and pulled itself out.

[ April 21, 2003, 03:17 PM: Message edited by: doug glasscock ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: POCO Power Cable to my house

torint,
It would be a good idea. To do it correctly, it is an expense, as you have to fill the ditch a foot or so over the conductors, lay in the marking tape and then complete the filling of the ditch. This almost doubles the labor hours requried for the backfilling of the ditch. The next issue would be where the conductors are installed by directional boring, would you require a second bore for the warning tape?
Don
 

charlie

Senior Member
Location
Indianapolis
Re: POCO Power Cable to my house

Actually, the conductors could be lowered. You really need to get the local electric utility involved. You may have damaged conductors that will fail in the future and will be billing the owner for your mistake. :(
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: POCO Power Cable to my house

Torint, the underground warning ribbon is a nice idea, but I have seen many times where the ribbon and conduct was dug through together. Also its hard to get the ditch backfilled half way and then put the ribbbon in. The backhoe folks want to cover and go.

But if you know its there, the ribbon is a heads up. the best way is to put sand around the cable or conduit, when you see the sand, you are almost there.
 
Re: POCO Power Cable to my house

tom i do agree with you about burying the power cables but the instering twist compound here in state of wisconsin the poco required the seconary line to be buryied at least 30 inches (3/4 meter) deep but if it is primary cables then therefore it go more deeper depend on voltage and classation (type) useally 3 1/2 to 5 1/2 feet deep i just have one job site the primary cables were buryed at 2 meter deep (6'7" ) it was 14.4 KV primary wye connetion then to underground transformer pad then termated the seconary line run at good 4 FEET deep ! it was 1600 amp 480 volts system


the gas pipe that do varis alot but it fall under national gas fuel code (aka natural gaz for multi puropse) for drop (from main line at street to the gaz meter it is will typically buryed at 2 1/2 feet for small one for large one it can go deeper for main run ( main gas line) it is buryed at 4 to 6 feet deep but it can varis depend on location ...

enough of my chatting here but main point is call the digger hotline or marking company to mark down all the uilites line etc before start digging etc .. ( state of wis say it is a law call 3 days before starting expect emgercy call will charge the trip to mark it down ) i am sure most other state do the same too


merci marc
 