newservice
- Syracuse NY
- Electrician extraordinaire
Apologies this is the NEC forum, but not sure where to post this. So I did a 100-200a service upgrade, contacted National Grid for a service order request and also a planner visit, as this is procedure when you change either the drop or the point of attachment. Looking at the drop it was obviously undersized even for 100a and original 1960 equipment, hence I requested the planner to visit and confirm the order to replace the drop with one adequate for the 200a service. By the way, the load calc clearly required 200a, 4000sf and electric range, an office 100a panel, addition had baseboard heat (larger than )AC, and a 60 breaker hot tub,..to name a few.
The Planner did visit and order the drop to be upgraded. Work was completed and inspected by the inspector I’ve used for 25 years.
The Line crew showed up ,with nobody there ,and changed the taps, sealed the meter, and ….left the old drop.
I complained to the Grid job “ owner” representative and said the Customer was aware, and I called the Planner, who was also upset as to why they would not comply with what she had ordered . She said it was not only very undersized, but an older brittle insulation type they seek to replace anyway. Planner reported it to her supervisor, who contacted the Line supervisor.
And that’s where it stood for a week. I then contact the rep, who said the Line sent someone to look, and reported it does NOT need to be changed.
In the past when I reach an impass like this I’ve had the Customer threaten to call the Public Service Commission, and that always worked. Apparently that is quickly becoming my last recourse.
This is more venting than question, but has anyone had similar experiences?