POE Lighting code requirements

Status
Not open for further replies.

clukes

New User
Location
Bozeman, MT, USA
Hello,

I am curious about POE lighting and what (if any) NEC rules apply. After digging around on the internet (lots of opinions and differing conclusions...), I found the following paper:

https://library.ul.com/wp-content/uploads/sites/40/2015/11/Power-over-Ethernet-white-paper_final.pdf

This seems to do a pretty good job of describing the various NEC and UL codes that apply, but I am curious about a few things that hopefully the experts around here can give their opinions on.

The latest POE spec (802.3bt Type 4) allows for 100W delivered by the PSE, with the PSE voltages between 52-57V. This is actually plenty of power for LED lighting applications.

My first set of questions are: Is POE lighting getting special treatment under NEC code by virtue of it riding on what was originally meant for information technology (computer) equipment? (Section 725.121 application allowances) Or, is the important aspect that POE lighting is just falling under the Inherently Limited Power Source portion of the code (Class 2 source, <100VA, <60V)?

My second set questions are: Would any Class 2 power source be ok to power LED panels/drivers? For example, could you use a 60VDC 100W Class 2 supply to power a hypothetical listed 60VDC LED Panel driver? Would something like Bell wire work (assuming the proper gauge size etc.)? Would CAT6 cable work (assuming you were distributing power in a similar way using the 4 pairs etc) even though you were not technically using Ethernet?

I see that some companies sell LED Panel drivers intended for remote install using class 2 plenum wires. This would seem to indicate that (assuming proper cabling for the install location), LED lighting powered by a class 2 supply, would not require conduits, etc. Correct?

One final note, it does appear that NEC 2017 does address issues specific to POE cable bundling.

Thanks,

Chip
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
I fail to see the advantage of large scale POE lighting at all. Power distributed on 24ga wiring within category cables can't be very efficient. I can't understand where this idea came from. What's wrong with powering the fixtures in the conventional manner with line voltage then run ethernet cables to provide the control?

-Hal
 
I fail to see the advantage of large scale POE lighting at all. Power distributed on 24ga wiring within category cables can't be very efficient. I can't understand where this idea came from. What's wrong with powering the fixtures in the conventional manner with line voltage then run ethernet cables to provide the control?

-Hal

While I also think Poe lighting is not practical at most scales, we desperately could use some sort of "plug and play" lighting system for grid fixtures. It's ridiculous how much time it takes to wire up a room full of 2x4's with mc and wire nuts...
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Actually I think that was tried several times over the years. Pre-made whips with plugs on the ends, daisy chain them together. It didn't became very popular. Still, I think manufacturers could make it easier to wire them without having to take them apart.

I don't know where the push for POE lighting is coming from but I have a hunch it's from IT and other LV people hoping to get into the lighting market.

-Hal
 

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
POE is intended to power things like remote cameras, key pads, phone terminals, and similar low-current devices, not 4' LED tubes replacing all of the fluorescents in a warehouse!

I think that LED wiring will end up running on POE voltages, but using more robust wiring. That would enable you to use low-voltage wiring rules.
 