On a service drop does the weather head have to be above the point of atchment?
I'm sure there are a few. :grin:I know it does if you have Consumers in Michigan.
230.54(C) Service Heads and Goosenecks Above Service-Drop Attachment. Service heads and goosenecks in service-entrance cables shall be located above the point of attachment of the service-drop conductors to the building or other structure.
I'm sure there are a few. :grin:
I am aware of the exception and it is a very poorly worded one as it does not actually say you can place the service head below the point of attachment, however I believe that is the intent of the section. That being said, it is a poor practice even where permitted. Under the right conditions if the splice is above the service head water can migrate down the space between the strands of the conductor and enter the equipment. This can happen even with a drip loop, unless the drip loop is formed in a shape that takes the top of the drip loop above the elevation of the splice.
Remember the poco sets the attachment point , they can put it where they want , if it gets flagged they have to move it , seldom will the ahj question it of course on a mast above a roof it has to be be tall enough , but there again the poco wont hit it anyway if it does not give clearance from ground.
Around here the electrician installs the point of attachment device not the POCO.
It doesn't really say you can install it below the point of attachment, but I agree that is what it means.Why would you argue with the code when it is giving you a way out by saying when it is impractical to locate the WH above the point of attachment , the only requirement is to locate within 24" of attachment.
As I said, unless the drip loop is formed in a manner that places the top of the drip loop above the splice point, it is possible for water to run in the spaces between the strands under the insulation and down into the service equipment. The water will enter the space under the insulation and can travel up to the same level as the end of the insulation at the point where the service entrance conductors are spliced to the service drop. The water will continue around the drip loop and down into the equipment unless the top of the drip loop is above the splice point. The possibility of this is greatly reduced where a compression connector of some type is use for the splice between the service drop conductors and the service entrance conductors.In my post I said leave a drip loop , I thought people would know what that means, it means the water would reach a low point and then have to travel up hill to get to WH
The power company is not covered by the rules in the NEC. They can place the point of attachment anywhere they want to. it is the electricians problem to put the service head in the correct location in relation to the point of attachment.This is a common practice on town houses on the gable end side where the drop crosses the highway , the attachment will be above the single 10 ft conduit for mast. I have never seen any one flagged for this , even with more than 2 ft from the WH. Remember the poco sets the attachment point , they can put it where they want , if it gets flagged they have to move it , seldom will the ahj question it of course on a mast above a roof it has to be be tall enough , but there again the poco wont hit it anyway if it does not give clearance from ground.
It doesn't really say you can install it below the point of attachment, but I agree that is what it means.As I said, unless the drip loop is formed in a manner that places the top of the drip loop above the splice point, it is possible for water to run in the spaces between the strands under the insulation and down into the service equipment. The water will enter the space under the insulation and can travel up to the same level as the end of the insulation at the point where the service entrance conductors are spliced to the service drop. The water will continue around the drip loop and down into the equipment unless the top of the drip loop is above the splice point. The possibility of this is greatly reduced where a compression connector of some type is use for the splice between the service drop conductors and the service entrance conductors. The power company is not covered by the rules in the NEC. They can place the point of attachment anywhere they want to. it is the electricians problem to put the service head in the correct location in relation to the point of attachment.
Around here the electrician installs the point of attachment device not the POCO.