Good day,
There is some debate going on about where is the first main disconnect to the hospital project i'm working on.
The UK engineers have added a new 5MVA 4160:480V transformer and associated switchgear to the building to meet the contractual obligations for redundancey. The project is in a British Overseas Territory, however the NEC is the adopted code for the jurisdiction.
The new system adds a new 5mVA 4160:480/277 transformer, diverts the oyutputs from the original 2.5mVA transformers to (2) "Changeover Panels" The new 5mVA transformer feeds both Changeover Panel A & B, the change overs are basically 4000A transfer switches for the utility feeds. These are ahead of all the building distribution, normal ATS s for Critical Branch Equipment Branch, Generator Sync Board etc.
MEDIUM VOLTAGE EQUIPMENT, DISCONNECT AND TRANSFORMERS ARE PROPERTY OF THE HOSPITAL.
INTENT OF TX-3 AND CHANGEOVER PANELS A & B IS IF EITHER TX1 OR TX-2 SHOULD LOSE ITS UTILITY FEED THE CHANGE OVER PANELS WILL TRANSFER THE LOAD TO THE TX-3 FEED AUTOMATICALLY. BASICALLY THE CHANGEOVER PANELS ARE TRANSFER SWITCHES ON THE UTILITY FEEDS.
THE QUESTION IS, IS THE SERVICE ENTRANCE POINT CHANGEOVER PANELS A & B IN THE NEW CONFIGURATION?
THE UK ENGINEER WANTS TO LEAVE THE NEUTRAL TO GROUND BOND IN THE MLV BOARD AND WE BELIEVE IT SHOULD NOW BE IN CHANGEOVER PANELS A & B .
Do these Changeover panels become the first main disconnects in the building. Turning off each of the 4000A switches in A & B disconnects the entire building from the utility.
I have a drawing I did for clarification, I just can't aatch to the thread.
There is some debate going on about where is the first main disconnect to the hospital project i'm working on.
The UK engineers have added a new 5MVA 4160:480V transformer and associated switchgear to the building to meet the contractual obligations for redundancey. The project is in a British Overseas Territory, however the NEC is the adopted code for the jurisdiction.
The new system adds a new 5mVA 4160:480/277 transformer, diverts the oyutputs from the original 2.5mVA transformers to (2) "Changeover Panels" The new 5mVA transformer feeds both Changeover Panel A & B, the change overs are basically 4000A transfer switches for the utility feeds. These are ahead of all the building distribution, normal ATS s for Critical Branch Equipment Branch, Generator Sync Board etc.
MEDIUM VOLTAGE EQUIPMENT, DISCONNECT AND TRANSFORMERS ARE PROPERTY OF THE HOSPITAL.
INTENT OF TX-3 AND CHANGEOVER PANELS A & B IS IF EITHER TX1 OR TX-2 SHOULD LOSE ITS UTILITY FEED THE CHANGE OVER PANELS WILL TRANSFER THE LOAD TO THE TX-3 FEED AUTOMATICALLY. BASICALLY THE CHANGEOVER PANELS ARE TRANSFER SWITCHES ON THE UTILITY FEEDS.
THE QUESTION IS, IS THE SERVICE ENTRANCE POINT CHANGEOVER PANELS A & B IN THE NEW CONFIGURATION?
THE UK ENGINEER WANTS TO LEAVE THE NEUTRAL TO GROUND BOND IN THE MLV BOARD AND WE BELIEVE IT SHOULD NOW BE IN CHANGEOVER PANELS A & B .
Do these Changeover panels become the first main disconnects in the building. Turning off each of the 4000A switches in A & B disconnects the entire building from the utility.
I have a drawing I did for clarification, I just can't aatch to the thread.