Point of Service

Status
Not open for further replies.
Re: Point of Service

From The FPL Electric Service Standards

Capitols and bolding by FPL

JUST A REMINDER!
FLORIDA STATUTE 812.14 STATES "IT IS UNLAWFUL TO WILLFULLY ALTER, TAMPER WITH, INJURE, OR KNOWINGLY SUFFER TO BE INJURED ANY METER, METER SEAL, PIPE CONDUIT, WIRE, LINE, CABLE, TRANSFORMER... OR TO ALTER THE INDEX OR BREAK THE SEAL OF ANY METER..."

PLEASE KEEP SAFETY FIRST -- CALL YOUR LOCAL FPL CONSTRUCTION OFFICE FOR AN APPOINTMENT TO DISCONNECT THE SERVICE AND REMOVE THE SEAL/METER. REFER TO SECTION III-I OF THESE ELECTRIC SERVICE STANDARDS REGARDING THE EXCEPTION ALLOWED BY FPL.
Exception:

FPL normally performs both the disconnect and reconnect. In certain cases however, the Customer's licensed and qualified electrical contractor is allowed, at his option, but only when approved by FPL, to perform the disconnect on overhead services only, when the following criteria are met:

- The Customer shall be a residential or small commercial facility with a main line switch rating of 300 Amps or less, served by an FPL single phase overhead service. No three phase service shall be disconnected by an electrical contractor. FPL must disconnect all three phase services to ensure that proper phase rotation is maintained.

- FPL service attachment point at the building or structure shall remain intact. No service shall be removed from the attachment point or the attachment point altered in any way.

- The meter socket(s) must not have an FPL locking device installed.

- If multiple meters are involved, the electrician shall "mark" each meter and socket.

- Only a licensed and qualified electrical contractor may perform the disconnect function and he shall schedule a reconnect date (appointment) with FPL before disconnecting the service. If the appointment is not made before the disconnect, FPL will not be responsible for a same day reconnect.

- The service shall be cut on the load side of FPL's connection to the customer's service conductors. No FPL conductors are to be cut.

- The service shall be disconnected before removing the meter(s). No meter is to be removed from an energized meter socket.

- FPL personnel only are to perform the reconnect and only after an inspection (if required by the local authority) is received. Electrical contractors are not allowed to reconnect the service.

- The decision to perform this type of disconnect is entirely voluntary for the electrical contractor and allows work to commence without having to wait for FPL to disconnect the service. However, the electrical contractor still has the option of FPL performing the disconnect if he prefers.
Make note of the part that says

No meter is to be removed from an energized meter socket.
 
Re: Point of Service

Jim, if someone doesn't pay an electric bill do you think the utility would have to keep giving them service?

The way they usually get the attention of the debtor is to cut off service by removing the meter or cutting the service conductors loose.

This could also be done in any type of illegal activity against the utility.

They could refuse to reconnect until any dues, fines, or deposits were satisfied.

If someone thought they could go cut a seal any time they wanted
If its my property how can you lock me out?
I think they would be in for a rude awakening.

If you had a utility or roadway easement across your property, you would find there are restrictions as to what you can and can't do here too, regardless of it being your property on paper.

Roger
 
Re: Point of Service

I have cut seals and removed meters for work on service equipment, troubleshooting etc. I just call and identify myself as a contractor, give the service address and meter No. and request a reseal. Haven't had any problems yet. Of course their policy could change any time.
 
Re: Point of Service

Not paying is hardly what we are talking about.
And cutting just anytime they wanted certainly would not be tolerated.
And my wife informed me our poco changed names from FP(NOT FPL) to PROGRESSIVE ENERGY ,i am trying to find there web page.
All im gonna say here is local poco are not saying anything about us cutting.As to Fl law i am trying to find there web page to read the entire 812.14 .Does seem if they pushed it we would need authorization,maybe in wrighting.

[ January 29, 2004, 08:30 PM: Message edited by: jimwalker ]
 
Re: Point of Service

John, your way is the correct way. This also coincides with Bob's post. The idea that "I own it" has no bearing on a utility allowing it or not.

Roger
 