Is a Disconnect required at a point of use HWH or instant hot water heater, As Manuf, by Eemax? If a disconnect is required can it be omittted if a breaker lock is used?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

An electric water heater is an electrical appliance and needs to have a disconnecting means in accordance with Part III of Article 422.

Chris
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I just noticed that this thread is in the "Proposals/Comments for the next NEC cycle" forum. I have decided to move it here where it is more applicable and will get more views.

Chris
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
Is a Disconnect required at a point of use HWH or instant hot water heater, As Manuf, by Eemax? If a disconnect is required can it be omittted if a breaker lock is used?

Per 422.31 (B), I would say a breaker lock would be adequate to satisfy the disconnect requirement.
 