The situation is a standard heavy-up with two wrinkles.
1) The meter can is in such bad shape that the PoCo doesn't want to even touch it while live, so it MUST be replaced.
2) The service lateral runs under the house (addition was put over it), so PoCo wants to move the meter from rear to side of house.
My dilema is that I'm a one-man show. Normally, I would just install the new meter and service and temp it with a long piece of SE cable until the PoCo comes back to put in the final lateral to the new location. Because of the meter location (about a foot off the ground) and it's condition, I can't do this. So, here's my plan.
I installed the new meter can, outside disconnect and feeder to the new service panel (the new panel is right next to the old working one).
My screwy plan is to move all the circuits from the old 100A panel to the new panel and do a temporary feed (#3 wires in Sealtite) from the old panel 100A CB to the new panel (into a backfed 100A CB with a retaining clip). So, the new panel will be a subpanel to the old panel for a week or two until I get it inspected and the PoCo does the final hook-up. On the day of the final hookup, I will remove the Sealtite feed.
The only possible violation of this setup that comes to mind during the temporary period would be the grounding. I did a 4 wire feed for the temp, so there is no parallel path, it's just a subpanel with it's own GES. I also locked the 200A main off in the new panel so it can't backfeed to the disconnect outside. I can't see this as a violation, but I hate doing something completely new without running it by someone first.
Let the rock throwing begin and thanks for reading all that.
Mark
1) The meter can is in such bad shape that the PoCo doesn't want to even touch it while live, so it MUST be replaced.
2) The service lateral runs under the house (addition was put over it), so PoCo wants to move the meter from rear to side of house.
My dilema is that I'm a one-man show. Normally, I would just install the new meter and service and temp it with a long piece of SE cable until the PoCo comes back to put in the final lateral to the new location. Because of the meter location (about a foot off the ground) and it's condition, I can't do this. So, here's my plan.
I installed the new meter can, outside disconnect and feeder to the new service panel (the new panel is right next to the old working one).
My screwy plan is to move all the circuits from the old 100A panel to the new panel and do a temporary feed (#3 wires in Sealtite) from the old panel 100A CB to the new panel (into a backfed 100A CB with a retaining clip). So, the new panel will be a subpanel to the old panel for a week or two until I get it inspected and the PoCo does the final hook-up. On the day of the final hookup, I will remove the Sealtite feed.
The only possible violation of this setup that comes to mind during the temporary period would be the grounding. I did a 4 wire feed for the temp, so there is no parallel path, it's just a subpanel with it's own GES. I also locked the 200A main off in the new panel so it can't backfeed to the disconnect outside. I can't see this as a violation, but I hate doing something completely new without running it by someone first.
Let the rock throwing begin and thanks for reading all that.
Mark