Pole Lighting Circuit Tripping Breaker After Several Hours Of Operation

Status
Not open for further replies.

Ravenvalor

Senior Member
I have a customer who has about 10 - sidewalk pole lights that trips the breaker after several hours of being on. They have standard medium base sockets with 10-watt LED lamps in them. Is there a way to find the short quicker than the method that I use? I usually open up the circuit about halfway, turn the lights on and wait to see if the circuit trips, if it does then I close the circuit back up and halve it again towards the breaker, I just keep doing this until I find the problem. As you can see, my method is very slow and cumbersome. I was wondering if someone would not mind sharing with me a quicker alternative. Perhaps temporarily replace the 10-watt lamps with 150-watt lamps?

Thanks for the help.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Don’t forget to remove all of the lamps if you meg it like @ptonsparky suggested. If it is a defective lamp, do the divide and conquer by replacing only half at first. Still not going to speed up your troubleshooting though. I’m assuming this is not 277 volt?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Have you checked the actual load? That sounds like a long time trip condition caused by the load or a poor connection at the breaker, or a fault with resistance high enough not to instantly trip. This could be a ground fault condition.
If this is the case, you can use an amp meter to help track down the fault. Current at the breaker, and then at the each light looking for a big drop in the amount of current.
 

Ravenvalor

Senior Member
Have you checked the actual load? That sounds like a long time trip condition caused by the load or a poor connection at the breaker, or a fault with resistance high enough not to instantly trip. This could be a ground fault condition.
If this is the case, you can use an amp meter to help track down the fault. Current at the breaker, and then at the each light looking for a big drop in the amount of current.
Thanks for the advice.
 

WaveGuide

Member
What type of breaker is it? Have you replaced the breaker? Breakers go bad and sometimes start to misbehave. This sounds to me like an intermittant breaker.

Also have you visually and tight checked the connections, all of them?
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
230410-1555 EDT

Ravenvalor:

You have a steady state load of about 1 A.

What is the size of your breaker?
If you measure the total input current to this string of lights, then what is the current after you first turn the lights on?
Then after the lights have been on for a while?
Does this current change much vs time?
What is the breaker manufacturer?

The current measurement should be made right at the breaker.

.
 

Ravenvalor

Senior Member
230410-1555 EDT

Ravenvalor:

You have a steady state load of about 1 A.

What is the size of your breaker?
If you measure the total input current to this string of lights, then what is the current after you first turn the lights on?
Then after the lights have been on for a while?
Does this current change much vs time?
What is the breaker manufacturer?

The current measurement should be made right at the breaker.

.
I will definitely make these tests.

Thank you
 