Haven't done street lighting in a while. Looking for a sanity check.
I've got a 900 foot stretch of roadway with 30 pole lights (lantern type on 12 foot poles). I'm going to run two 240V circuits and pick up every other fixture on the two circuits. I plan to run #6's which more than compensates for any Voltage drop concerns.
Typically I don't run less than 2" conduit underground for anything. So that's the plan. I also don't see a need for handholes, opting instead to pull from pole base to pole base (is that a mistake? I certainly don't want to have a HH per fixture).
If I'm to run the 2 circuits through each pole base as is the plan, I can't see putting 2 2" conduits in the pole base. For 40% fill, I do need 1 1/4 inch.
That being the case, I'm thinking I should probably just go with the 1 1/4 across the board in lieu of 2 inch.
Anything wrong with my thinking on this? I appreciate your input?
Thanks,
Mike
I've got a 900 foot stretch of roadway with 30 pole lights (lantern type on 12 foot poles). I'm going to run two 240V circuits and pick up every other fixture on the two circuits. I plan to run #6's which more than compensates for any Voltage drop concerns.
Typically I don't run less than 2" conduit underground for anything. So that's the plan. I also don't see a need for handholes, opting instead to pull from pole base to pole base (is that a mistake? I certainly don't want to have a HH per fixture).
If I'm to run the 2 circuits through each pole base as is the plan, I can't see putting 2 2" conduits in the pole base. For 40% fill, I do need 1 1/4 inch.
That being the case, I'm thinking I should probably just go with the 1 1/4 across the board in lieu of 2 inch.
Anything wrong with my thinking on this? I appreciate your input?
Thanks,
Mike