jazer
Senior Member
- Location
- Gibsonia, Pa
I have a situation that is confusing me. A house needs a 200 amp service upgrade, the meter is mounted 50 feet away from the structure on a pole. So, the entrance conductors will be 4/0 SE cable on the pole to the meter, the secondary of the meter into the house will be an underground method, yet to bedetermined, feeding a 200 amp main breaker panel. My confusion starts here, the meter on the pole is a seperate structure, needing its own GES. OK, so drive a pair of rods and bond to grounded terminal inside meter. Now, why do I feel like running only three conductors into the house from the meter is not correct? Once in the house at the first disco, another GES must be created, using waterline and again driving rods. This doesn't seem right to me and I am having a hard time defining all of this in the code. Also, i believe the POCO will not want those rods bonded in the meter socket.... So, who would be the AHJ, POCO or inspector who may define that pole mounted meter as a seperate structure? Thanks.