The two primary bushing (big ones on top) trans can be connected either line to line (high voltage) or line to neutral on a wye distribution line (not so high voltage) depending on the line voltage and voltage class of the transformer. If it is going to be connected line to neutral, it is cheaper to use a trans with one end of the primary connected to a lug on the side. One less bushing, Usually lower insulation class winding etc.
So it depends on what is required for the service, what the loads are on the number of phases which are on the poles. There may only be one phase there, so the only connection possible is line to neutral. Branch lines are like this out here in the country. Or there may be 3 phases and the residential services are all on one and the commercial is supplied open wye/open delta 3 phase from the other two. That is how it is on the main line from the substation down our way. I think this is partly because the 3rd phase was only recently installed and because it keeps any flicker from the commercial customers starting motors etc. from affecting the residential.
someone else may have other reasons to add. I'm like you, I want to know if I look at the transformer bank, if one has a wire burnt off it or what.
Jim
edited to add primary to the description of the bushings.