I was asked to review a water pump electrical substation transformer internal fuse rating and to specify the time coordination between the transformer internal fuse and the fuse link at the pole. Let me provide the specifications and the engineering approach I used for a possible recommendation. I am just looking for a sanity check.
Tansformer voltage secondary: 488/277
Transformer voltage primary: 13.8 KV
Transformer VI: 500 KVA
Transformer manufacturer: Cooper Power system
Internal bayonet primary fuse provided: 50 amps
Basis for the rating :ANSI/IEEE XXXX: transformer hold 160% of full load for 6 hours without blowing out. It also monitors transformer oil temperature.
Time interval for the fuse to blow .1 -.4 sec.
The client would like to see .4 seconds coordination between the internal fuse and the pole fuse link.
After reviewing the current - time curve for the bayonet fuse at .1 sec, I came up with 1500 amps.
Next, I talked to the Cooper and Bussman application engineers to get current curve for fuse link of K ant T type. After I reviewed those curve the only way I could get the .4 second coordination is if I use 150 amps fuse link K class. My belief is that .4 second coordination is too long of a time interval.
a .1 second or 100 millisecond coordination could be obtained with a fuse link of the K type at 80 amps and should be sufficient for this application.
I am in the process of reviewing the internal bayonet fuse for time delay to handle the motor locked rotor and start current ( both are about the same.
Thanks for any feedback.