So the main feeder to the panel 1C needs to come from a 2 pole breaker...2 Hots? If so what would indicate that....3W??? The single phase part is what throws me.No 3-wire means H-H-N. It's 1Ø, 120/240. Circuits 1/3 and 5/7 are 2-pole CB's.
Single phase can be a 2-pole breaker if it is 240V, or 208V, etc. Single phase just means it's not 3ph. You have to look at the voltage to determine if it needs a single pole or 2-pole breaker. Example: 120V always is a single pole, 240V would be a 2-pole. If it takes two legs of a system, then it needs a 2-pole. 277V might be a little confusing as it comes from 480V, but is single ph and only needs a single pole breaker.So the main feeder to the panel 1C needs to come from a 2 pole breaker...2 Hots? If so what would indicate that....3W??? The single phase part is what throws me.
Look at the details given in the notes:So the main feeder to the panel 1C needs to come from a 2 pole breaker...2 Hots? If so what would indicate that....3W??? The single phase part is what throws me.
Industry slang rears it ugly head.So the main feeder to the panel 1C needs to come from a 2 pole breaker...2 Hots? If so what would indicate that....3W??? The single phase part is what throws me.
Thank youHave you checked out these free videos? Very good for trying to get up to speed on the complex subject of electricity. I used these extensively when I was going from carpenter to inspector (not that long ago).
https://www.youtube.com/@ElectricianU/videos - Sometimes oversimplifies things, but better at explaining the more general points to help beginners. Also good for seeing how to actually wire a 3-way switch or taking one apart to see how it works. Much more of a hands-on teacher. His code knowledge/interpretations are more geared to how the jurisdictions he works in translate the code, so some of them are a little different from what would be a mainstream interpretation.
https://www.mikeholt.com/tv-safety.php - These videos go more in-depth. The electrical safety fundamentals series is very good. Heavy on theory. Code information is very reliable.
ThanksLook at the details given in the notes:
Main Lug
125 Amp bus
120/240
1 Phase
3-Wire
This means that you have two hots and a neutral. The feeder to this panel would therefore require a 2-pole circuit breaker.