I have a old existing 240v 3 wire uf feeder to a pump house that is about 3 feet from a natural pond. The customer wants to add a 240v 20a outlet on the outside of the pumphouse to feed a new aerator. The aerator would be on a 24hr timer inside the pumphouse. The way I interpret 682 is that only equip. installed outside would require an equipotential plane. If all the equip. were inside except the receptacle the pump would plug into then an equipotential plane is not required. Then the only req. would be a GFI breaker for the pump?
The other rabbit snare is that now we would be changing the panel for the pumphouse and the pumphouse is right next to the pond. This new panel will be wired to service only line to line loads. According to 682.11 it needs to be 5' from the shoreline, do you think that means the building or the actual equipment inside? To me it may be a AHJ call seeing as it is an existing building. Any comments?
The other rabbit snare is that now we would be changing the panel for the pumphouse and the pumphouse is right next to the pond. This new panel will be wired to service only line to line loads. According to 682.11 it needs to be 5' from the shoreline, do you think that means the building or the actual equipment inside? To me it may be a AHJ call seeing as it is an existing building. Any comments?