I've got issues w/a DP gfi breaker nusiance tripping. The (load) motor is on 125 ft. of cable (floating fountain), tied into j-box with appx. 460 ft of #6 cu.,
circuit conductors, 2" pvc (buried). Clock timer, motor cap. box and OC breaker at panel. The DP 30 gfi breaker trips randomly. Motor load is appx. 10.2 amps
@250 volts. The fountain motor is 2hp.,single phase. Can't figure out why gfi breaker trips so infrequently. Definitely not ovr. load. Could it be capacitance
issue. Fountain company meg'd the ckt. and thinks the conductor insul. is the problem of which we've already replaced. Any thoughts and help?