I realize you must get inundated with calls about weird electrical findings and people asking what to do about it. I hope you might find the time to think about our results here.
We have an outdoor, in-ground, gunite and plaster pool at an apartment complex. There was a report (we were not able to get the report directly) from one of the bathers that they felt a “tinkle” when they believe they were in the area of the pool light. I believe the light was off at the time.
We decided to do a bonding and grounding test on the structure. Here is what we found on our initial arrival:
The pump and heater were bonded together with a #8 wire that also went to one of the copper suction lines of pool.
We did not see any copper wire going into the ground.
There was no #8 tied to the circuit breaker panel within the pump room.
There was normal ground leads within the breaker panel and the pump and heater.
The pool light junction box was not a normal “pool light” junction box. It was a usual 4 square box. The conduit containing the light’s cord was pvc and does not look original.
There is a #8 wire coming out of the ground outside the light conduit and ties to the 4 sq box.
There is a #8 insulated green wire within the light conduit coming into the 4 sq box and tied to the common electrical bar there.
There is a ladder and a handrail (metal) mounted to the deck and drop into the pool’s water.
We tested for both resistance and NEV. First we ran a cable from certain points of the equipment/ladder/handrail/light on the ohms scale. We then drove a screw driver into the ground, far from any electrical service, and took voltage measurements to various pieces of the equipment. We got what we considered to be very confusing results. I have list them below:
Voltage – Measuring from dirt/screwdriver to . . . . . .
Handrail 0.024 volt
Ladder 0.014 volt
Light body 0.014 volt
#8 bare copper
wire at light J box 0.014 volt
Pump and heater
#8 wire 0.014 volt
Time clock box 0.014 volt
Concrete decking
(wet) within 3 ft
of pool edge 0.012 volt
Water in pool 0.029 volt
Breaker panel 0.014 volt
Gas pipe 0.093 volt
Probe in air 0.005 volt
We then measured the resistance from various points to other points within the pool area. We got:
Water to:
Handrail 1.103 Mohm
Ladder 3.338 Mohm
Light body negative 0.293 kohm
Pump/heater negative 0.393kohm
Time clock negative 0.360 kohm
Breaker panel negative 0.324 kohm
#8 bond wire at
light J box first was at OL then went to negative 0.296 kohm
Then tried handrail to:
Ladder 2.95 k ohm
Light body negative 2.205 kohm
Pump/heater #8
bond wire Negative 2.206 kohm
time clock negative 2.150 kohm
Breaker panel negative 2.1665 kohm
#8 bond wire at
light J box Negative 2.205 kohm
The tried ladder to:
Light body Negative 3.305 kohm
Pump heater #8
bond wire negative 3.420 kohm
Time clock negative 3.42 k ohm
Breaker panel negative 3.470 kohm
#8 bond wire at
J box of light negative 3.305 k ohm
I am assuming there must have been some voltage present to give us a negative reading on the ohm scale. But I cannot make any meaning out of it. Off hand I can reasonably assume the deck, handrail, ladder and light body are not fully bonded. It also appears there is a break in the #8 wire that comes from the ground at the light’s J box for the pool light.
I am sure the pool was built prior to the rule establishing the need to bond the decking around the pool shell. So I am kind of ignoring that for now. There have not been any complaints other than the unsubstantiated report of the pool light tingle.
What pattern I am missing here?
Thanks in advance for your help.
Sincerely,
Dave Ferraresi
DF/mc
We have an outdoor, in-ground, gunite and plaster pool at an apartment complex. There was a report (we were not able to get the report directly) from one of the bathers that they felt a “tinkle” when they believe they were in the area of the pool light. I believe the light was off at the time.
We decided to do a bonding and grounding test on the structure. Here is what we found on our initial arrival:
The pump and heater were bonded together with a #8 wire that also went to one of the copper suction lines of pool.
We did not see any copper wire going into the ground.
There was no #8 tied to the circuit breaker panel within the pump room.
There was normal ground leads within the breaker panel and the pump and heater.
The pool light junction box was not a normal “pool light” junction box. It was a usual 4 square box. The conduit containing the light’s cord was pvc and does not look original.
There is a #8 wire coming out of the ground outside the light conduit and ties to the 4 sq box.
There is a #8 insulated green wire within the light conduit coming into the 4 sq box and tied to the common electrical bar there.
There is a ladder and a handrail (metal) mounted to the deck and drop into the pool’s water.
We tested for both resistance and NEV. First we ran a cable from certain points of the equipment/ladder/handrail/light on the ohms scale. We then drove a screw driver into the ground, far from any electrical service, and took voltage measurements to various pieces of the equipment. We got what we considered to be very confusing results. I have list them below:
Voltage – Measuring from dirt/screwdriver to . . . . . .
Handrail 0.024 volt
Ladder 0.014 volt
Light body 0.014 volt
#8 bare copper
wire at light J box 0.014 volt
Pump and heater
#8 wire 0.014 volt
Time clock box 0.014 volt
Concrete decking
(wet) within 3 ft
of pool edge 0.012 volt
Water in pool 0.029 volt
Breaker panel 0.014 volt
Gas pipe 0.093 volt
Probe in air 0.005 volt
We then measured the resistance from various points to other points within the pool area. We got:
Water to:
Handrail 1.103 Mohm
Ladder 3.338 Mohm
Light body negative 0.293 kohm
Pump/heater negative 0.393kohm
Time clock negative 0.360 kohm
Breaker panel negative 0.324 kohm
#8 bond wire at
light J box first was at OL then went to negative 0.296 kohm
Then tried handrail to:
Ladder 2.95 k ohm
Light body negative 2.205 kohm
Pump/heater #8
bond wire Negative 2.206 kohm
time clock negative 2.150 kohm
Breaker panel negative 2.1665 kohm
#8 bond wire at
light J box Negative 2.205 kohm
The tried ladder to:
Light body Negative 3.305 kohm
Pump heater #8
bond wire negative 3.420 kohm
Time clock negative 3.42 k ohm
Breaker panel negative 3.470 kohm
#8 bond wire at
J box of light negative 3.305 k ohm
I am assuming there must have been some voltage present to give us a negative reading on the ohm scale. But I cannot make any meaning out of it. Off hand I can reasonably assume the deck, handrail, ladder and light body are not fully bonded. It also appears there is a break in the #8 wire that comes from the ground at the light’s J box for the pool light.
I am sure the pool was built prior to the rule establishing the need to bond the decking around the pool shell. So I am kind of ignoring that for now. There have not been any complaints other than the unsubstantiated report of the pool light tingle.
What pattern I am missing here?
Thanks in advance for your help.