Sparky1981
PE
- Location
- Denver, CO
- Occupation
- Electrical/Lighting Engineer
I am working on an existing Recreation Center that has an existing lap pool. This lap pool is 40 years old and does not contain the equipotential grid. We are adding a large wing to the aquatics to include a new leisure pool, water slide, hot tub and therapeutic pool. Of course all these pools were designed with an equipotential grid that all metal parts to these pools will bond to.
My question is the AHJ is considering making the contractor provide this grid for the existing pool. To me this is a huge cost. With this pool not in scope I did not include it on my plans. Two questions
1. Is there an exception anywhere in the 2011 NEC I am missing for an existing pool?
2. Assuming we need to provide this has anybody had to do this on an existing pool? How did you do it? I am thinking of things like the metal drain at the bottom of the pool, how the heck to you bond that to a grid in an existing deck.
Thanks in advance.
My question is the AHJ is considering making the contractor provide this grid for the existing pool. To me this is a huge cost. With this pool not in scope I did not include it on my plans. Two questions
1. Is there an exception anywhere in the 2011 NEC I am missing for an existing pool?
2. Assuming we need to provide this has anybody had to do this on an existing pool? How did you do it? I am thinking of things like the metal drain at the bottom of the pool, how the heck to you bond that to a grid in an existing deck.
Thanks in advance.