Pool box.

Status
Not open for further replies.

RolandoMir

Member
Location
Miami, Fl
680.24 Junction Boxes and Electrical Enclosures for Transformers or Ground-Fault Circuit Interrupters.
(A) Junction Boxes. A junction box connected to a conduit that extends directly to a forming shell or ............

My question is:
Why does the NEC require a pool box?.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What would you use if you didn't need a junction box? For a wet niche fixture the box is above the water level to keep the water draining out of the pool.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
A pool box has a number of unique points enhancing pool safety that are not present in a standard PVC or metallic box.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
It is wet-niche and operates above the low voltage contact limit.
You sure that this is "above the low voltage contact limit"? That would be rare today as almost all pool lights are low voltage today even though the code still recognizes 120 volt lights. And now that I think of it, in Miami-Dade county don't they prohibit 120 pool lights?
 

rnatalie

Senior Member
Location
Catawba, NC
Occupation
Retired Electrical Engineer
And now that I think of it, in Miami-Dade county don't they prohibit 120 pool lights?
Wouldn't be a bad idea. We still lose a person or two a year due to bad pool lights.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
From the NEC handbook. The box they are talking about is the one I show here.


View attachment 2554561


I have never seen a pool light box like that one shown. The ones we see are brass..

1555436734837.jpg
 

rnatalie

Senior Member
Location
Catawba, NC
Occupation
Retired Electrical Engineer
I think the NEC graphic is purely figurative. You are correct, the one you show is the classic pool box design.
 