Does an Intermatic time clock (with the manual shutoff lever) satisfy the requirement for 680.12?
Originally posted by charlie b: I infer from your description that the manual shutoff lever will turn off the equipment, regardless of the state of the clock.
This is the key issue. How does the device work? Will it, in fact, turn itself back on when the timer times out, or will the manual lever disable the timer? To satisfy 680.12, the disconnect device must de-energize the circuit forever, or until a person intentionally turns it back on, whichever comes first. If there is a timed, automatic re-start, then sandsnow would be right.Originally posted by sandsnow: If you shut off the manual lever, it will turn itself back on automatically.
What you quoted is not code language. It is EC&M's explanation. Refer to 680-12 in the code. The discn. must be ....located within sight of all pool, spa, and hot tub equipment...(partial NEC quote)Originally posted by dana1028:
680.12 - Maint. Disconnecting Means - they state the following:
"...The disconnecting means must open all circuit conductors to the equipment so that it will be totally de-energized when the disconnecting means is in the "OFF" position. If the equipment is a motor, then the disconnecting means must also be rated in horsepower, or be a circuit breaker."
hmmm - does anyone know where this language comes from? (in the code).
I apologize for the 1999 code sections. Were not on the 2002 yet.Originally posted by sandsnow:
What you quoted is not code language. It is EC&M's explanation. Refer to 680-12 in the code. The discn. must be ....located within sight of all pool, spa, and hot tub equipment...(partial NEC quote)Originally posted by dana1028:
680.12 - Maint. Disconnecting Means - they state the following:
"...The disconnecting means must open all circuit conductors to the equipment so that it will be totally de-energized when the disconnecting means is in the "OFF" position. If the equipment is a motor, then the disconnecting means must also be rated in horsepower, or be a circuit breaker."
hmmm - does anyone know where this language comes from? (in the code).
There is nothing about "all circuit conductors" which would lead you to believe a grounded conductor (if present)would need to be disconnected. Also the discn. means as per 430 does not need to be HP rated as long as it is 115% of FLC in Table 430-148 Also see exception to 430-110. Although 430-102(b) EXC permits the discn. means to be remote and lockable, 680-12 which is specific to pools would further modify the discon. means. Just as 440-14 is more restrictive for discn. means for A/C equip.