I am looking at a job that requires a 130'run from the main service panel in the home to a pool house.
Pool contractor wants a 60 amp sub feed quoted for the job.
With all pool equipment, a small kitchenette and a small AC unit I come up with close to 40 amps.
Am on the fence between pulling #4 or #6 thhn.
#6 would suffice, but VD comes into play..
#4 would cover it but then I'm upsizing raceway from 3/4 to 1"
120/240V single phase is the voltage
Opinions welcome.