Went to check on a condo pool equipment room as the chemical pumps (120v) were not functioning properly. After checking voltage and finding a back feed decided I better start unwiring some things and isolate the circuit. Found 2 conductors under ground that had burnt and were completely separated. They were conductive through the water in the conduit, enough to make a reading on my meter and also back feed on the next conductor. Pulled new circuits wired everything up turned it on and the pumps failed to work. Turned the circuit off and got whacked by the neutral?
Turns out the previous, so called electrician, failed to bond the XO terminal on the transformer. I’m really glad I found the real problem as i keep thinking this could have been a devastating event…
Now I want to rewire the whole room.