Steve Courtney
I am working on a commercial pool constructed in the early 1970's. The 200 amps electrical service to the building included the pool equipment area and 2 heat pumps rated at a minimum ampacity of 39 Amps each {50 amps max circuit ampacity}.
A load calculation indicated a 260 amp connected load. The HOA wants to add more to the building's service so I engaged in a contract with them to remove the pool heaters from the existing service and connect them to a separate service (for the heat pumps) thereby opening up the building's service for additional connections.
The new heat pump service was installed and approved by the local BD with the following exception: Pool bonding was not verifiable and they are trying to require us to meet the current code requirements for the 2008 code cycle.
Here is our issue. ARTICLE 680.26
(2) Perimeter Surfaces. The perimeter surface shall extend for 1 m (3 ft) horizontally beyond the inside walls of the pool and shall include unpaved surfaces as well as poured concrete and other types of paving. Bonding to perimeter surfaces shall be provided as specified in 680.26(B)(2)(a) or (2)(b) and shall be attached to the pool reinforcing steel or copper conductor grid at a minimum of four (4) points uniformly spaced around the perimeter of the pool. For nonconductive pool shells, bonding at four points shall not be required.
(a) Structural Reinforcing Steel. Structural reinforcing steel shall be bonded in accordance with 680.26(B)(1)(a).
CURRENTLY THE STEEL IS ENCASED IN A POOL SHELL THAT HAS NO APPARENT LEAKS, THEREFORE "(b)" is our only apparent choice:
(b) Alternate Means. Where structural reinforcing steel is not available or is encapsulated in a nonconductive compound, a copper conductor(s) shall be utilized where the following requirements are met:
(1) At least one minimum 8 AWG bare solid copper conductor shall be provided.
(2) The conductors shall follow the contour of the perimeter surface.
(3) Only listed splices shall be permitted.
(4) The required conductor shall be 450 to 600 mm (18 to 24 in.) from the inside walls of the pool.
(5) The required conductor shall be secured within or under the perimeter surface 100 mm to 150 mm (4 in. to 6 in.) below the sub grade.
THE EXISTING POOL DECK IS 30 FEET WIDE ON ONE SIDE AND 5 FEET WIDE ON THE REMAINING THREE SIDES. HOW CAN THE AHJ REQUIRE US MEET THIS CODE?
WHEN DOES AN ALTERATION HAVE TO BE BROUGHT UP TO MEET ALL EXISTING CODES?