We came upon a pool/hot tub installation this week where there was a 60 amp feeder to a sub-panel for the pool. The 60 amp feeder is GFCI protected with the contractor thinking that would suffice for all pool/hot tub GFCI requirements (excluding existing outlets, etc)
To me the fact that 680.23 (A)(3) speifies "GFCI in the branch circuit" would mean the underwater lighting requires a GFCI in the branch circuit.
Other than that, can anyone think of an area where branch circuit GFCI protection is required as opposed to feeder GFFCI protection ?