I have a pool guy trying to put a GFCI breaker in a panel that feeds a pool timer, and pump. (This house built in the late 80's BTW) Well, the GFCI breaker trips, probably due to a solar panel controller being tapped on the load side of timer, along with the pump. Controller and pump are both 240 volts. He is telling the home owner that there is a ground fault, and the pool equip. cannot be turned on until corrected. Im telling the home owner that there is no ground fault, and the original, regular, breaker is code complaint for the year the house was built. I do know that GFCI protection on this pool equipment, would now be required if in new construction. I can reconfigure everything to do so, but is this really a code violation in this old house?
Thanks for any input.
I have a pool guy trying to put a GFCI breaker in a panel that feeds a pool timer, and pump. (This house built in the late 80's BTW) Well, the GFCI breaker trips, probably due to a solar panel controller being tapped on the load side of timer, along with the pump. Controller and pump are both 240 volts. He is telling the home owner that there is a ground fault, and the pool equip. cannot be turned on until corrected. Im telling the home owner that there is no ground fault, and the original, regular, breaker is code complaint for the year the house was built. I do know that GFCI protection on this pool equipment, would now be required if in new construction. I can reconfigure everything to do so, but is this really a code violation in this old house?