Does current code require GFCI protection for a heat pump on an inground pool?
The unit is 208/230 V single phase. Max breaker size 50A per nameplate.
What about an installation in 2008, would it have been required then?
Thank you.
That has changed a bit in the 2017 NEC680.21(A)(1) requires branch circuits for pool associated motors to have an insulated copper EGC. Don't know if they would intend that to include a heat pump compressor or not.
680.21(A) Wiring Methods. The wiring to a pool motor shall comply
with (A)(1) unless modified for specific circumstances by
(A)(2), (A)(3), (A)(4), or (A)(5).
(1) General. Wiring methods installed in the corrosive environment
described in 680.14 shall comply with 680.14(B) or
shall be type MC cable listed for that location. Wiring methods
installed in these locations shall contain an insulated copper
equipment grounding conductor sized in accordance with
Table 250.122 but not smaller than 12 AWG.
Where installed in noncorrosive environments, branch
circuits shall comply with the general requirements in Chapter
3.
680.28 Gas-Fired Water Heater. Circuits serving gas-fired
swimming pool and spa water heaters operating at voltages
above the low-voltage contact limit shall be provided with
ground-fault circuit-interrupter protection for personnel.