Hello everyone. Went to someone's house and it looks like a pool heat pump was installed after the house was built.
It was either installed 2014 NEC or 2017 NEC. House was built in 2018. North Florida. In 2018 they were going off of 2014 NEC. The homeowner can't give me a direct answer because she said she bought the house with the pool heat pump already there.
It's a 220V. Min circuit ampacity of 43.26 amps. Max breaker is 60 amps. Has copper 6/2 "Romex" (max 55 amps).
If this was a brand new install, I wouldn't posting this.
2014 NEC does specifically state for pool heat pump circuits 50 amps or less. It looks like 2014 NEC might have have required GFCI protection for a pool heat pump. Something about under 150 volts would require GFCI protection.
Just sit on one website I would read, "150 volts".
On another website I would read, "150 volts to ground". This means each leg to ground (not across) the legs.
If I'm interpreting this right, it looks like (under 2014 NEC) pool heat pump would require GFCI protection.
Please help me interpret this. I went to public schools in Alabama
It was either installed 2014 NEC or 2017 NEC. House was built in 2018. North Florida. In 2018 they were going off of 2014 NEC. The homeowner can't give me a direct answer because she said she bought the house with the pool heat pump already there.
It's a 220V. Min circuit ampacity of 43.26 amps. Max breaker is 60 amps. Has copper 6/2 "Romex" (max 55 amps).
If this was a brand new install, I wouldn't posting this.
2014 NEC does specifically state for pool heat pump circuits 50 amps or less. It looks like 2014 NEC might have have required GFCI protection for a pool heat pump. Something about under 150 volts would require GFCI protection.
Just sit on one website I would read, "150 volts".
On another website I would read, "150 volts to ground". This means each leg to ground (not across) the legs.
If I'm interpreting this right, it looks like (under 2014 NEC) pool heat pump would require GFCI protection.
Please help me interpret this. I went to public schools in Alabama