Re: Pool heater and Pump Installation
How large is your pool? How long will the circuit feed be from the house to the pool? I am just concerned about the heater and motor circuit. If you run with UF cable table 310.16 states the ampacity of #6 AWG UF to be 55 amps and 680.9 states "the branch circuit conductors for the heater shall not be less than 125% of the total nameplate rated load". What is your nameplate rated load? There might even be some adjustment factors that have to be calculated. The best help I would give you is hire an electrician, your kids will love you for it and you will sleep better. I am just an apprentice, but when I am in doubt I ask my journeyman........