Pool Heater

Status
Not open for further replies.

Mjohnson2586

Member
Location
NY
Occupation
Electrician
I came a crossed a pool heater today that was failing I believe. The crazy thing is that is was only a 120v pool heater but it was causing the entire service to be unbalanced i.e. there was 90v on A phase and 150v on B phase. This is only the cause when pool heater is running. I tested everything at meter with heater off and it checks out.

Can any one tell me why this is. Besides there might be a heating coil going bad.
 
Typical of a poor neutral on service. Will usually present like this with loads applied otherwise would look normal. Likely the phase with drop would shift if you put the load on the opposite line.
 