At a residence, Would a detached pool house with a kitchen require AFCI protection ?
 
At a residence, Would a detached pool house with a kitchen require AFCI protection ?

IMO, no-- it is not a dwelling

210.12(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-
ampere branch circuits supplying outlets or devices installed in
dwelling unit kitchens, family rooms, dining rooms, living
rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, laundry areas, or similar rooms or
areas shall be protected by any of the means described in
210.12(A)(1) through (6):
 