pool light circuit
philmc
New member
I have a individual 120volt lighting circuit that comes out of the electrical panel to a wall controled s/p switch controling a light fixture in the swimming pool and a light in the Spa pool. It does not have a transformer to lower the voltage to less than 15 volts. It does not have ground fault protection. I was told the local authority says there is no need for the ground fault circuit to the lights. Is this correct?
The pool light must be GFCI protected art. 680.23(A)(3)
You should also read 680.22 & 680.23 There are probably other violations
Dennis , that would only be true, depending on how you would relamp the fixture. 680.23 1 says you don't need to GFCI protect the fixture during normal use ( not relamping). However I do agree that if I were installing it I would put it on a GFCI.
Okay, so how would you ensure safety when you had to relamp other than a GFCI. I must admit I always thought GFCI was required but now I am thinking. That means trouble.
I have seen fiber optic lights that were installed away from the pool with just the fiber optic line to the pool. In this case, I believe no GFCI is necessary.
i don't install gfci on fiber optic pool lighting; there are no current carrying conductors at the pool. a 120v light installed in the shell of the pool is definitely getting gfci protection.
I believe we are all in agreement on that. :)