george t. everett

Senior Member
Location
New York
What is the proper way to terminate the the grounding conductor (16 stranded)of a wet niche pool light? Under a screw in the junction box or a wire nut to the # 12 solid? Under a screw seems to damage the strands.
 
Re: Pool light GC

In accordance with 680.23(B)(3), "...This grounding conductor shall be connected to a grounding terminal in the supply junction box, transformer enclosure, or other enclosure..."

This implies it must be on a grounding terminal. :(
 