Pool Light LED switched from 15 amp General lighting circuit

Status
Not open for further replies.

J R

Member
House built 2017 under the 2011 NEC. The electrician came off the living room 15 amp afci breaker protected outlet. Well they ran 14-2 romex from receptacle added switch and ran to pool light transformer then changed to #12 wire in conduit to pool light j box. The pool light cord only has 2 wire no ground that's ok because Pentair makes a glow bright no metal fits in 2' pvc. My question is it legal to do this the code states and manufacturer #12 wire minimum I have never done a pool light without at least a #12 ground wire run to the pool light J box. Well I have not wired a pool for at least 10 years. It is difficult to keep up with all the code changes especially now led lighting is the thing. Funny because pool panel is next to transformer I would have just ran the 50ft of 12/2 to inside of house switch....
 
Dennis do you or anyone have the nec 2011 specific code article number in 680 that refers to #12 minimum size ground wire
 
Dennis do you or anyone have the nec 2011 specific code article number in 680 that refers to #12 minimum size ground wire

Min #12 awg copper
insulated equipment ground
no wire nuts for the branch circuit equipment ground (positive pressure connection)
 
Here is the wording to the sections mentioned above

(F) Branch-Circuit Wiring.
(1) Wiring Methods. Branch-circuit wiring on the supply
side of enclosures and junction boxes connected to conduits
run to wet-niche and no-niche luminaires, and the field
wiring compartments of dry-niche luminaires, shall be installed
using rigid metal conduit, intermediate metal conduit,
liquidtight flexible nonmetallic conduit, rigid polyvinyl
chloride conduit, or reinforced thermosetting resin
conduit. Where installed on buildings, electrical metallic
tubing shall be permitted, and where installed within buildings,
electrical nonmetallic tubing, Type MC cable, electrical
metallic tubing, or Type AC cable shall be permitted. In
all cases, an insulated equipment grounding conductor
sized in accordance with Table 250.122 but not less than
12 AWG shall be required.
Exception: Where connecting to transformers for pool
lights, liquidtight flexible metal conduit shall be permitted.
The length shall not exceed 1.8 m (6 ft) for any one length
or exceed 3.0 m (10 ft) in total length used.
 