Pool light transformer keeps tripping gfic breaker

Status
Not open for further replies.

Patwano

Member
Location
Tunkhannock,PA
New install of 12v nicheless 20w pool light connected to 100 watt listed transformer, 20 amp Eaton br gfic breaker,,,,breaker trips whenever switch is turned on even with no load on transformer (light disconnected) ,,, transformer and breaker are new,,never ran into this before with square d breakers,,,,bad transformer or bad breaker??
 
place a different load on the light circuit in place of the transformer. If it trips it is a problem with the wiring . otherwise it is the transformer.
 
Try it with the primary disconnected at the transformer, and then try swapping the transformer primary conductors. Also, try the transformer on another circuit.
 