mvannevel
Senior Member
- Location
- Hesperia, Michigan
This is kind of long, but bear with me. Inspected a pool last week. The "conduit" extending from the forming shell of the wet niche fixture to the junction box was soft drawn copper tubing. The fittings on the ends were 1/2" slip by 1/2" MPT. And, of course, it contained the flexible cord. The electrician told me that this is what the pool installer puts in for all of his fixtures and no other inspector has ever questioned it. I don't claim to be an expert on pools, but I've inspected a few over the years and have never seen copper tubing run to a pool fixture. Only brass or PVC. I told the electrician that as long as someone could supply me with something that showed that's how the fixture was listed to be installed, I'd accept it. In checking with inspectors in neighboring jurisdictions, I find that they have been approving this installation. My understanding here is that metallic conduit (or the #8 insulated conductor in non-metallic conduit)is the equipment grounding conductor. When and how could copper tubing with fittings soldered on the ends be considered an equipment grounding conductor? This would seem to violate 250.8, since the fittings rely solely on solder. The pool contractor has a dozen different reasons for using the copper tubing. He says (alternately) that the #8 conductor and lug corrode, that PVC or any other conduit freezes and breaks causing the pool to leak, that rigid brass conduit doesn't exist, and on and on. He can't supply me with a listing that shows copper tubing as an listed wiring method for these lights. Bottom line is that the copper is cheap and quick to install. I intend to bring this question up at our Metro Inspectors meeting next week, but would appreciate your input on this. Is there something here that I'm missing? If I'm wrong about this, fine, I just want this to be a safe, code compliant installation.