Pool Lite Conduit Depth

Status
Not open for further replies.

george t. everett

Senior Member
Location
New York
Table 300-5 allows Residential branch circuits rated 120 volts, GFI protected, Max 20 amp OCP to be buried a minimum of 12 inches. Does this apply to conduits feeding wet niche fixtures in a swimming pool?
 
yes you can use table 300.5 for that pool light conduit, IMO table 680.10 applies to underground conduit that does not supply pool equipment
 
George,

Outside of the 5' area 300.5 applies, inside of the 5' area, using the space

limatation provision, T 680.10 kicks in.
 