I'm wiring an above ground pool. Motor has a regular 120 volt straight blade plug.
Inspector told me it has to be a twist lock but I don't see that anywhere in the book.
Did I miss it?
I did install a weather/ tamper resistant duplex on a GFI breaker.
Any advice?
I don't know what code cycle you are under but the 2017 (maybe earlier) changed. 680.22(A)(1) used to say the pumps had to be 10' from the pool but could be not less than 5' if certain conditions were met. The locking receptacle was one of the requirements.
Now in the 2017, the pump motor or circulation equipment is in 680.22(A)(2). It changed to just 6' with no exceptions for being any closer. Also, no mention of a locking receptacle.
You are either on an earlier version of the code or your inspector isn't aware of the change.
In the 2014 NEC (A)((1)(2) was dropped. That being said, I believe the twist-lock receptacle was required so that the plug wouldn't fall out due to vibration. From what I remember the pool motors were shipped in from the manufacturer with a std. 15A plug and a 15A cord. We had to change both the cord to a 20A SO cord as well as the plug to a 20A twist lock. Although it's no longer required I still think it's a good idea to make this change IMHO.680.22 Lighting, Receptacles, and Equipment.
(A) Receptacles.
(1) Circulation and Sanitation System, Location. Receptacles that provide power for water-pump motors or for other loads directly related to the circulation and sanitation system shall be located at least 3.0 m (10 ft) from the inside walls of the pool, or not less than 1.83 m (6 ft) from the inside walls of the pool if they meet all of the following conditions:
(1) Consist of single receptacles
(2) Employ a locking configuration
(3) Are of the grounding type
(4) Have GFCI protection
This is from the 2011 NEC:
In the 2014 NEC (A)((1)(2) was dropped. That being said, I believe the twist-lock receptacle was required so that the plug wouldn't fall out due to vibration. From what I remember the pool motors were shipped in from the manufacturer with a std. 15A plug and a 15A cord. We had to change both the cord to a 20A SO cord as well as the plug to a 20A twist lock. Although it's no longer required I still think it's a good idea to make this change IMHO.
I don't think it was for vibration else they would have required them for a 10' away install. I think the locking feature was due to the exception of allowing the recep closer than 10' so you couldn't use the plug for general use.
OK, I can buy into that line of thinking but Jap brings up a couple of good points.I don't think it was for vibration else they would have required them for a 10' away install. I think the locking feature was due to the exception of allowing the recep closer than 10' so you couldn't use the plug for general use.
OK, I can buy into that line of thinking but Jap brings up a couple of good points.