C Crabcakes&football Member Location Florida Occupation Electrician Nov 13, 2024 #1 Looking for the code reference. I have pool lights 12vdc, need the code that says It doesn't require gfci protection.
Looking for the code reference. I have pool lights 12vdc, need the code that says It doesn't require gfci protection.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Nov 13, 2024 #2 680.23(A)(3)
C Crabcakes&football Member Location Florida Occupation Electrician Nov 13, 2024 #3 I have a 20amp non gfci breaker going to my pool lights driver. Then obviously from there it's going to the pool lights.
I have a 20amp non gfci breaker going to my pool lights driver. Then obviously from there it's going to the pool lights.
C Crabcakes&football Member Location Florida Occupation Electrician Nov 13, 2024 #4 augie47 said: 680.23(A)(3) Click to expand... I believe that's it, thank you. I currently don't have my book with me.
augie47 said: 680.23(A)(3) Click to expand... I believe that's it, thank you. I currently don't have my book with me.