I’ve seen the #8 pool bond run back a couple times to the pool subpanel now. Am I correct and saying it is not required, but not prohibited either?
Not required, but no prohibited then either if someone did it as I seen, correct680.26(B) states:
"An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes."
Rob G
Seattle
Yes it is not prohibited, just a waste of time, material, and money.Not required, but no prohibited then either if someone did it as I seen, correct
I agree. I have seen it twice recentlyYes it is not prohibited, just a waste of time, material, and money.