Re: POOL POST LIGHT /LOAD SIDE OF GFI
Originally posted by mudcat555:
GEORGESTOLZ, My reason for the gfi feeding the high pressure sodium light, is to be compliant with code 680-6 (b) (2). I sunk a 12 foot wolmanized post 4 foot into the ground to overcome Ohio's winter frost line, leaving the fixture height at 8 foot above ground, 4 foot above pool water level.
Teach me for not seeing "NEAR A POOL" in your original post.
Looking on...
680.22(B) Luminaires (Lighting Fixtures), Lighting Outlets, and Ceiling-Suspended (Paddle) Fans.
(1) New Outdoor Installation Clearances. In outdoor pool areas, luminaires (lighting fixtures), lighting outlets, and ceiling-suspended (paddle) fans installed above the pool or the area extending 1.5 m (5 ft) horizontally from the inside walls of the pool shall be installed at a height not less than 3.7 m (12 ft) above the maximum water level of the pool.
(4) GFCI Protection in Adjacent Areas. Luminaires (lighting fixtures), lighting outlets, and ceiling-suspended (paddle) fans installed in the area extending between 1.5 m (5 ft) and 3.0 m (10 ft) horizontally from the inside walls of a pool shall be protected by a ground fault circuit interrupter unless installed not less than 1.5 m (5 ft) above the maximum water level and rigidly attached to the structure adjacent to or enclosing the pool.
So, if your fixture is within 5' of the pool, it would have to be 12' in the air, but no GFI protection is required. If it's between 5' and 10' away, it would require GFI protection if it were less than 5' above max water level.
How far away is your fixture?
Again, this is working off the 2002, which, judging from the mass of change-bars along this text, I'd imagine it could be wildly different.
Now, I'll step aside and let someone qualified answer.
[ August 30, 2005, 11:09 PM: Message edited by: georgestolz ]