So, pools are not my strong suit but I would like to improve on that. Situation, 100A Panel on separate structure, Pool House, at a SFD is currently fed with 4 conductors, bare ground not connected, AL, in 2? PVC from House to the Pool House.
We are under the 2008 cycle
I have about 90? inside the House from the Main panel then outside for about 60? to the Pool House underground. There are currently all sorts of phone and other metal between the House and the Pool House.
My question:
Can I run a #2 CU SER inside the House to a box where I transition to the outside then pull 3 #3 THHN/THWN and an INSULATED #8 THHN/THWN underground to the Pool House panel protected by a 100A 2p breaker in the Main panel?
Drive a ground rod at the Pool House and, of course, separate the Neutral and EGCs. The Pump Motor is hardwired and there is no bonding jumper from the pump motor to the panel or Equipotential grid. I think there should be.
I look forward to your help.
We are under the 2008 cycle
I have about 90? inside the House from the Main panel then outside for about 60? to the Pool House underground. There are currently all sorts of phone and other metal between the House and the Pool House.
My question:
Can I run a #2 CU SER inside the House to a box where I transition to the outside then pull 3 #3 THHN/THWN and an INSULATED #8 THHN/THWN underground to the Pool House panel protected by a 100A 2p breaker in the Main panel?
Drive a ground rod at the Pool House and, of course, separate the Neutral and EGCs. The Pump Motor is hardwired and there is no bonding jumper from the pump motor to the panel or Equipotential grid. I think there should be.
I look forward to your help.