Re: Pool pump dedicated ground
Bill I think your talking about the Equal potential bonding conductor?
There is no requirment in the NEC to run this conductor back to the service grounding. This conductor is not for grounding but to just keep all metal that is within 5' of the pool at the same "equal" voltage. While connecting it to the GE might not cause a hazard it could cause a problem if the service grounded conductor (neutral) lost connection. This could put a voltage to earth on all the metal bonded by this conductor. But then so could the required connection to the pump EGC?
Please read 680.26 in the "2002" NEC.