today i went to troubleshoot a pool pump that was shocking
the homeowner.
pump motor had jumpers set for 240.
it was on a 2P 15 amp breaker. zinsco circa 1960's.
house is knob and tube, from 1923 ish.
one of the hot wires and the ground were reversed
inside the peckerhead. yes, the case of the motor,
the pump housing, and all the water was at 115 volts
potential. had been that way for three years since
they had someone replace the pump.
the pump was running on 115 volts, with jumpers set
for 240, for three years.
and it didn't trip the 2P 15 amp zinsco breaker.
amazingly enough, it didn't burn out the pump motor either.
i could run my voltage pen along the PVC leaving the pump,
and it glowed brightly. i put a 2k shunt DVM between the pump
housing, and a lead dipped into the pool water, and it was 114 volts.
this wasn't a static or ghost voltage. it was measured across a 2k ohm load.
their was a purge hose with a hose bib on top of the discharge pipe from
the pump, and if you opened the hose bib so the water coming out of the
pump came out the hose, and it splashed on you, it would shock you,
according to the homeowner. measuring from the bronze hose bib teed off
the plastic pipe, to the pool water, was 115 volts.
and nobody got killed. three years.
the homeowner.
pump motor had jumpers set for 240.
it was on a 2P 15 amp breaker. zinsco circa 1960's.
house is knob and tube, from 1923 ish.
one of the hot wires and the ground were reversed
inside the peckerhead. yes, the case of the motor,
the pump housing, and all the water was at 115 volts
potential. had been that way for three years since
they had someone replace the pump.
the pump was running on 115 volts, with jumpers set
for 240, for three years.
and it didn't trip the 2P 15 amp zinsco breaker.
amazingly enough, it didn't burn out the pump motor either.
i could run my voltage pen along the PVC leaving the pump,
and it glowed brightly. i put a 2k shunt DVM between the pump
housing, and a lead dipped into the pool water, and it was 114 volts.
this wasn't a static or ghost voltage. it was measured across a 2k ohm load.
their was a purge hose with a hose bib on top of the discharge pipe from
the pump, and if you opened the hose bib so the water coming out of the
pump came out the hose, and it splashed on you, it would shock you,
according to the homeowner. measuring from the bronze hose bib teed off
the plastic pipe, to the pool water, was 115 volts.
and nobody got killed. three years.