--BEWARE-- According to Hayward, their variable speed, computer controlled, pool pumps create a significant amount of electrical noise when they start up and that noise is put on the power conductors going to the pump. As a result, some GFCI circuit breakers will trip as soon as the pump attempts to start. Hayward Tech Support recommends that Siemens GFCI breakers be used, although they do not identify that in their literature. I know for a fact that the Cutler Hammer BR GFCI breakers will not work with the pumps, but I do not know if the GE or Square D breakers will work or not. I personally have had problems with the CH BR breakers and have had no problems with the Siemens.
Siemens sells a SPA panel with a 60A GFCI breaker (QF260) installed (W0408L1125SPA60) and the same panel without the breaker (W0408ML1125U) that can be used a small sub-panels.
I have not received any indication from Hayward that they intend to do anything about the pump generated electrical noise.
Siemens sells a SPA panel with a 60A GFCI breaker (QF260) installed (W0408L1125SPA60) and the same panel without the breaker (W0408ML1125U) that can be used a small sub-panels.
I have not received any indication from Hayward that they intend to do anything about the pump generated electrical noise.